I discovered something. The problem wasn't entering ISP mode.
I have been able to connect to the Lpc2103 only using the monitor utility of FlashMagic, not the normal sequence. I followed the lpc2103 user manual, using the "? <CR><LF> sequence, and get sinchronized after many many attempt.
Introduced the string "Synchronized<CR><LF>" and so on.
In this way was possible to erase all sectors and unlock the CRP as I
needed. The point is that probably the cycle of attempt done by
FlashMagic and Sill is not able to syncronize the Lpc2103. It has to be
done "manually" , looking at the answer....
Has anybody tried those utilities with Lpc2103 already? As I wrote the
same Lpc2103 behaviour is shown by my new board and an Olimex starter
kit.
Any commment could be useful
thanks again , Mauro